Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

How to configure Alarm Escalation in Security Expert.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to configure Alarm Escalation in Security Expert.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support
  • AdamSteele
    AdamSteele

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2034 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to configure Alarm Escalation in Security Expert.

Picard Product_Support
‎2018-09-10 07:22 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 08:39 PM

Issue

Alarms need to be sent to specific Workstations and then escalated to other Workstations if they have not been acknowledged within a specific amount of time.

Product Line

EcoStruxure Building Expert

Environment

Security Expert

Cause

Documentation does not describe specific steps for how to configure alarm escalation.

Resolution

You will be able to do the alarm escalation with Security Expert by using the Alarm Routing options under the Events Menu.

1. Create your Workstations by going to Events | Workstations. The name of the new Workstation object in Security Expert will need to correspond to the actual Windows PC name for alarms to be routed properly.

SX_Events_Worsktations.jpg


2. After you have created all of the Workstations you will need to create Workstation Groups under the Events menu. One group for each level of alarm routing that you want to do. If you have three workstations and want to route from one to the next to the next, then you would need to create three Workstation Groups and add one Workstation to each of them.

SX_Events_WorsktationGroups.jpg


3. Next you will need to create an alarm routing list under Events | Alarm Routing. On the Workstation Groups tab add the time for Transfer After (this is in seconds) which is when the alarms will be routed to the Workstations in the next Workstation Group. Set the Routing Order for those groups, the first group is 0. Next set the Transfer Priority if you have specific alarms that are to be routed to these Workstation Groups, leave blank if all alarms are to be routed. Set the routing group active to enable routing.

SX_Events_AlarmRouting.jpg


4. The last bit is to go to your Alarms that you want to route and add the routing list you created in step 3 to the Alarm Routing List field. This will now route these alarms to the Workstations you've configured.

SX_Events_Alarms_AlarmRoutingList.jpg

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • 19763
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of