How to Relinquish a BACnet point/value at a given priority
  • How to Relinquish a BACnet point/value at a given priority
  • David_Kendrick
    David_Kendrick
  • AbeMeran
    AbeMeran
‎2018-09-06 01:20 PM
Last Updated: Sisko GavinHe Sisko ‎2022-10-10 03:14 AM
A Schedule or PE program can not change the value of a point because it is set by another process at a higher Command Priority.
Andover Continuum
  • CyberStation
  • bCX4040
  • B3s
Command value must be Relinquished at the priority that no longer needs to control the point's value so that a command with a lower priority can take control of it.
Edit the point from the BACnet view.
Go to the Command Priority tab, this tab shows the 16 priorities and their current statuses
Select the priority to relinquish and then click on the Relinquish button.
The command with the next highest priority should then immediately take over.