Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How much broadcast (i.e ARP) traffic can Continuum controllers handle before they turn off their transceiver and go offline.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How much broadcast (i.e ARP) traffic can Continuum controllers handle before they turn off their transceiver and go offline.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran
  • JohnBoehmer
    JohnBoehmer
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2548 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How much broadcast (i.e ARP) traffic can Continuum controllers handle before they turn off their transceiver and go offline.

Product_Support
‎2018-09-11 10:15 PM

Last Updated: CraigEl Champion ‎2022-08-14 07:43 PM

Issue

Offline alarms received from Continuum controllers every few minutes and log error 0x00006c0e Broadcast Storm AKA Error transmitting and/or 0x00006c03 Driver fatal error during operation.

MyErrorLog.png

Product Line

Andover Continuum

Environment

Continuum Net Controller II

Continuum ACX 4 Controller

Continuum CX Gen 1

Continuum bCX4040

Continuum bCX9640

Continuum BCX4000

Cause

Excessive ARPs and/or other broadcast traffic on the network.

Resolution

When troubleshooting controller offline issues that are suspected to have excessive broadcast traffic as the root cause it is important to understand how to interpret Wireshark capture to determine whether too much broadcast on the VLAN  is indeed the problem.

Note that taking the percentage of broadcast traffic in a Wireshark capture while a good starting point cannot in itself be solely used as proof that excessive broadcast is indeed the root cause of the controllers going offline, this is because in the absence of much unicast traffic the broadcast traffic will make up most of the packets resulting in a misleading high percentage.

A much better way to determine whether the controller maybe going offline due to excessive broadcasts is to look at the average broadcast packets per second over a 15-20-minute capture.

The screen capture below shows the statistics from a 20 minute capture filtered by broadcast traffic (eth.dst == ff:ff:ff:ff:ff:ff) 

ARPsBEFORE.png

The capture shows that about 63% of the traffic is made up of broadcast at an average of 24 packets per second.

The Continuum controllers on the network were going offline multiple times an hour.

Note that the Continuum controllers are initially able to handle a much higher rate of broadcast traffic, tests performed in the PSS lab show a CX9680 can handled about 10 times  the amount shown here sustained for 5-10 minutes but over a much longer period of time such as several days or weeks the amount of broadcast traffic shown was enough to cause the controllers  to go offline.

The screen capture below shows the statistics after the root cause of the excessive broadcast was identified and fixed.

ARPsAFTER.png

The problem at the site in question here was a defect in the network switch that was making the switch duplicate ARP traffic.

CiscoSwitchBUG.png

Note that Cisco switch model Catalyst 4500 is also effected by the firmware bug.

Current version which fixed the issue:

Catalyst 4500 L3 Switch  Software (cat4500e-UNIVERSALK9-M), Version 03.08.05.E RELEASE SOFTWARE (fc2)

 

Previous version which caused the broadcast problems:

Catalyst 4500 L3 Switch  Software (cat4500e-UNIVERSALK9-M), Version 03.08.02.E RELEASE SOFTWARE (fc2)

Labels (1)
Labels:
  • Andover Continuum
Tags (5)
  • Find more articles tagged with:
  • 19650
  • 6c03
  • 6c0e
  • AbeMeran20
  • ARP
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore