Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How many AV's and BV's are able to be created in a SmartStruxure Lite MPM?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How many AV's and BV's are able to be created in a SmartStruxure Lite MPM?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1341 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How many AV's and BV's are able to be created in a SmartStruxure Lite MPM?

Picard Product_Support
‎2018-09-07 11:01 AM

Issue

The MPM-UN controller comes with 100 AV's and 100 BV's. These may be added to the current database of the controller for various programming needs. However, when SE7000 controllers are added, they consume 14 of these AV's each (this is with the 2.5.6 firmware, which limits the ZigBee window to 14 AV points). The AV points are quickly gone from the MPM stock, and once 100 AV's are used, there are no more for further programming.

If programming is done first, this is no problem, because the addition of SE7000 devices will continue to consume the remaining AV's from the original 100 available, then create AV's over 100 once the original are gone. How many AV's are available until the controller just doesn't recognize them, or stops allocating them to additional SE7000 controllers?

Environment

MPM-VA

MPM-UN

MPM-GW

Cause

As standard the library of objects in Building Expert displays 100 AV and 100 BV objects, however more are available but it is not clear how to access them.

Resolution

An MPM has capacity for up to 700 AV's and 700 BV's. Once the initial 100 are consumed, you can add Value Banks of 100 each AV and BV. Value Banks are added as devices and will be listed as sub devices under the main MPM.

To add a Value Bank:

1. In the Building Expert Explorer panel, select the Add Devices icon . A new window opens.

2. Select Value Bank to add this your Controller. Added Device shows in Device to add column.

3. Click Add Devices button.

4. Repeat steps 2 - 3 to add any additional Devices.

5. Click Close

Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (1)
  • Find more articles tagged with:
  • 14965
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.