Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How Continuum ReportCmdLine achieve email delivery of a Continuum report.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How Continuum ReportCmdLine achieve email delivery of a Continuum report.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • JohnBoehmer
    JohnBoehmer
  • Alan_Wood
    Alan_Wood
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1658 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How Continuum ReportCmdLine achieve email delivery of a Continuum report.

Picard Product_Support
‎2018-09-06 12:51 PM

Issue

Does Outlook need to be installed or running in order for ReportCmdLine to deliver email reports.

Does ReportCmd interact directly with the Exchange server.

Environment

  • Continuum
  • CyberStation
  • WebClient
  • Outlook
  • Report
  • ReportCmdLine
  • Exchange

Cause

Troubleshooting problems with email delivery of reports.

Resolution

The ReportCmdLine.exe has no interaction with Exchange mail services whatsoever.  It simply notifies the report object specified by the /o argument that the report should be created and sent in the form of an email, or a file, or both.

The effect is similar, though not precisely the same as opening the report object and selecting the Email button on the tool bar.
These two actions, i.e. sending a report email using by selecting the report email button or by using the ReportCmdLine's  /t argument differ in the following way.

Report Email button:
The report Email button embeds the report HTML in an email.
The report email must then be sent manually.
If Outlook is not installed on the workstation, selecting the email button generates an error Send Mail failed to send message.

ReportCmdLine:
When the report object receives the email argument from the ReportCmdLine.exe it creates a report email.
The email cannot be sent until Outlook is running.
If Outlook is not running the Continuum caches the report email so that it can be sent once Outlook is up and running.
If Outlook is not running the ReportCmdLine batch file will not display a failure error.

In either case you need a mail client that supports Enhanced MAPI protocol (MS Outlook) installed and running on the Cyberstation in order to deliver the report via email.  Since Continuum is not an Exchange client it cannot interact directly with and Exchange server.

Note: If the customer doesn't like the DOS box showing when the report runs.

Run DOS minimized by using start/min in a batch file  Ex. Start /min Myreport.bat

Note: There has been a case where having Google Chrome as the browser has affected the sending of automatic reports. Removing it corrected the issue. This was not reproducible in PSS.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 6994
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore