Getting error unhandled exception when trying to run a report of extended log data
  • Getting error unhandled exception when trying to run a report of extended log data
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • AbeMeran
    AbeMeran
‎2018-09-10 08:33 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-10 01:43 AM
Andover Continuum
CyberStation
ACCTrace reveal workstation is handling excessive extended log data (>100,000 lines in ACCTrace in a couple minute)
In the CyberStation properties, set the 'Download extended log data from Controllers on the LAN' to false.
Reboot CyberStation
If reports runs ok now the Extended logging configuration should be revised.
See Extended Logging gaps, performance and load balancing for more information.
  • 7180