Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Getting error Unable to find Extended Log records to download

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Getting error Unable to find Extended Log records to download
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • PaulFr
    PaulFr
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2644 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Getting error Unable to find Extended Log records to download

Picard Product_Support
‎2018-09-10 11:34 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:39 PM

Issue

Extended log data not being saved to the database. Error stated that controller should be returned online and reloaded.

Product Line

Andover Continuum

Environment

  • Cyberstation SQL Extended log data
  • Extended logging Error
  • Troubleshooting logs

Cause

Error is generated indicating a mismatch between the Database and controller. But reloading the point does not always cure the problem.

Resolution

The error Unable to find Extended Log records to download states that it was added to the point when the controller was off-line.

This can often be the case and the controller should be returned online and reloaded. However if this does not resolve the problem there are other extended logging issues that can cause this message:

  1. Ensure the system is set to be using Enhanced alarm logging and delivery if the system is V1.5 or above, it should have been configured (in the DB initialisation) to use this. See Alarm Forward and Log settings with enhanced alarm logging causes unnecessary network traffic.
  2. Run the Continuum analyser to ensure the database is not corrupt. Fix any issues and reload the controller.
  3. The controllers have not been fully reloaded. Ensure that a full reload including all attached controllers has been done and that this does not generate any errors.
  4. Ensure software and firmware is compatible for the version you are using, see Compatibility matrix. Also check Operating system versions and .Net versions are correct for the version used.
  5. Verify that you have set the same UTC times for the country in the Network, all Workstations and all BACnet controllers.
  6. Check that one Workstation has the time synchronisation program running to keep the CX's in sync' (Time sync controllers to workstations). Look at the Continuum error log to make sure you are not getting Extended log time synchronisation errors.
  7. Check for network problems; use the Controller offline alarm to verify no controllers go offline. Controller Network problems can stop the objects from saving to the controller which will cause a mismatch between the DB and controller requiring a reload.
  8. Ensure the Workstation IP address is a fixed address in the Windows settings and it matches the Workstation IP address in the database, as viewed in Offline Editing.
  9. Verify only 1 network card is fitted and enabled in the PC.
     
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 8282
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore