Issue
A network level controller is shown offline. Can a flash upgrade (Update OS) be done to it?
Product Line
Andover Continuum
Environment
- BCX
- ACX5720 ACX5740
- NC2
- CX9900
Cause
A bCX needed a flash upgrade but was offline in CyberStation. How can we update the OS?
Resolution
The Update OS function can sometimes be completed even if the controller indicates that it is offline.
If it cannot be pinged from CyberStation, it will not likely be able to be upgraded in its current state and may require returning for repair.
But if it can be pinged it, try doing the Update OS.
Follow the progress in the Distribution window. If it completes, the controller will likely come back online a few minutes after the update is complete
Completing this "Blind Update OS" can often restore to normal operation a controller that has its Operating System corrupted not allowing the Web page to be accessed, as long as you know the ACCNet ID and IP address (a reset IP can be performed) this process may be attempted.
It is also possible to flash an offline controller if it has reverted to the default IP address (169.254.1.1) and ACCNet ID of 1 if the Workstation is set to be in the same subnet so it can ping the controller and these default settings are used for the controller configuration.
If after a full cold restart and at least 2 attempts to flash the controller fail, then the controller may need to be returned for Repair.
Some possible causes of this problem are listed in What can cause a controller to reset, cold start or lose data.