Issue
- Initiating a Find New Bacnet Device will not bring 3rd party device into the system.
- Can successfully find BACnet device using another front end system.
Environment
Cyberstation
Cause
Workstation device node ID set to 1
Resolution
The workstation Device Node ID must be set to a unique value and cannot be duplicated by any other device.
Best practice is to make the Device Node ID equivalent to the CyberStations ACCNetID when creating the workstation in Continuum Database Initialization.