Issue
Filtering Alarms in StruxureWare Building Operation to show only I/NET alarms
Product Line
EcoStruxure Building Operation, TAC INET
Environment
I/NET integrated to StruxureWare Building Operation version 1.9 and older
Cause
Users may wish to only view alarms from the I/NET system
Resolution
Filter for All I/NET Alarms:
- Create an alarm View
- Click on the Filter Object
- Add a condition to Filter by Type
- Select the Type 'INET Alarm Record'
- Click OK
Filter for I/NET Alarms from a Specific Link
- Create an alarm View
- Click on the Filter Object
- Add a condition to Filter by Source
- Type */INET Interface/LL where LL is the link number of the desired link. Note: If the INET interface on your server is not the default name, the name must match yours exactly.
- Click OK