Failure when upgrading Reader Expander module firmware
  • Failure when upgrading Reader Expander module firmware
  • RobertAndriolo
    RobertAndriolo
  • AdamSteele
    AdamSteele
  • David_Kendrick
    David_Kendrick
Guinan AdamSteele Guinan
‎2020-07-28 05:04 PM
Performing a firmware upgrade on a reader expander module via the SP-C's web page will fail with the message:
"Error - The module failed to restart in boot mode"
Firmware update failureFirmware update failure
EcoStruxure Security Expert
SP-C, SP-RDM2, SP-MRDM2.
Cause 1
  • There was an intermittent communications fault hindering the update process.
Cause 2
  • There are Smart Card Readers connected to the reader expander module, which are set to RS485 communication.
  • This appears to be causing RS485 communication issues between the SP-C and the reader expander which is hindering the firmware upgrade process.
For Cause 1
  • Run the module upgrade process again.
For Cause 2
  • Physically remove all connected RS485 Smart Card Readers from the reader expander module being upgraded.
  • Once the reader expander firmware has been successfully upgraded, reconnect all Readers.
  • EcoStruxure Security Expert