Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Failed to establish connection with server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Failed to establish connection with server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
11464 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Failed to establish connection with server

Picard Product_Support
‎2018-09-06 11:48 AM

Last Updated: Picard RobertAndriolo Picard ‎2023-05-01 05:35 PM

Issue

When attempting to log into a server, the error message "Failed to establish connection with server" appears.

WorkStation-FailedtoEstablishConnection.png

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Workstation
  • Building Operation Servers

Cause

WorkStation is unable to make a connection to the desired server for one of several reasons.

Resolution

Unable to log into the Enterprise Server

  1. Verify that the Enterprise Server is running
    1. Go to Start Software Administrator
    2. Verify that the Server Status is Running. If it is stopped, then click the Start Service button, and click OK.
      SoftwareAdmin-ServerStatus.png
    3. Log into the server through Workstation.
  2. Lockout after restoring a backup set
    1. If an enterprise server backup set has just been restored, it may take several minutes for the server to return online, depending on the database size.
    2. Wait for the server to come back online and try logging in again.

Unable to log into the Automation Server

  1. Verify the Ethernet connection
    1. Go to Run > cmd.
    2. Ping the IP address of the automation server. If it fails to communicate to the controller, verify that the ethernet connections are good and that there are no IT issues.
  2. Lockout after restoring a backup set
    1. If an automation server backup set has just been restored, it may take several minutes for the server to return online, depending on the database size.
    2. Wait for the server to come back online and try logging in again.
  3. Verify the IP address
    1. Go to Device Administrator 
    2. Connect to the Automation Server with a USB cable.
    3. Select the automation server once it is visible in the Device Administrator window and click on its name.
      DeviceAdmin-USBConnection.png
    4. Note: If the device indicates "Password Required," - Login into the automation server (default login is admin, and password is admin).
    5. Once the details open - Select the Ethernet 1 Configuration option and verify or enter the IP address details.
      DeviceAdmin-EthernetConfig.png
    6. After applying the information, enter this IP Address in WorkStation "Server" option to log on. 
      WorkStation-Server.png

For further troubleshooting help see the following online help topic: Failed to Establish Connection

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 11137
  • RobertAndriolo23
Was this article helpful? Yes No
80% helpful (4/5)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore