Having trouble communicating to an NPR or other I/NET hosts over a slow/busy ethernet.
TAC INET
Any Version of Windows OS and Any Version of I/NET Seven
You can make I/NET more tolerant of communication delays over the IP network by making the following change.
  1. Open regedit.
  2. Browse to HKEY_LOCAL_MACHINE\SOFTWARE\CSI - Control Systems International\I/Net 2000\Configurations.
  3. Select your active profile.
  4. On the right side, right click and modify the DWORD value "EthernetTimeout" and click "Decimal".
  5. The default value is 500mS or half of one second. Increasing this value will determine how long I/NET waits for a response over the ethernet before it gives up. Raise it to 1000, 2000, 2500, etc. and see if it helps.
  6. For additional information please see NPR's giving you "Host Lost - Host Restore" messages.