When attempting to run LonMaker, the following errors may occur in succession:
  • Could not listen on poet/tcp: The address specified is already in use (Error -2532)
  • Database error:
    (Subsystem: LNS, #25) [DB #-2506]
    The global database is not open.
    (Subsystem: LNS, #64)
Additional errors that may be caused by the same underlying issue:
  • Problem connecting with the database server process:
    (Subsystem: LNS, #36) [DB#-2523]
  • Error opening LCA Global database
EcoStruxure Building Operation, Satchwell BAS & Sigma, TAC IA Series, TAC Vista
  • LonMaker for Windows 3.1 and 3.2
  • Sentinel Protection Installer 7.6.1
The issue is typically caused by a conflict between the Sentinel Protection Server and the POET Server, as both attempt to use the same port(s).
  • Sentinel Protection Installer 7.6.1 installs the Sentinel Protection Server, which manages Sentinel SuperPro and UltraPro keys used with Satchwell Sigma and other products
  • This service is not required for the dongle driver to function and can interfere with LonMaker’s operation.
Refer to:
Error: LNS #25 lcaErrDatabase for more technical details.
To resolve the issue:
  1. Stop the Sentinel Protection Server:
    • Open the Windows Services console:
      • Press Windows + R, type services.msc, and press Enter.
    • Locate Sentinel Protection Server.
    • Right-click and select Stop.
  2. (Optional): Disable the service if not needed:
    • Right-click > Properties > Set Startup type to Disabled.
✅ This will allow POET Server to operate without port conflicts.