Error registering Plug-ins: Plug-in 'TACOSSysPin.Document' launch failure

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Error registering Plug-ins: Plug-in 'TACOSSysPin.Document' launch failure
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1488 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Error registering Plug-ins: Plug-in 'TACOSSysPin.Document' launch failure

Picard Product_Support
‎2018-09-07 09:24 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 04:58 PM

Issue

Error when trying to register plug-ins within an LNS environment. Two known examples:

TACOSSysPin.png

Plug-in 'TACOSSysPin.Document' launch failure.
Unknown error 0X8007002

 

ExceptionOccurred.png

 Plug-in 'TACOSSysPin.Document' launch failure.

Exception occurred

Product Line

TAC Vista

Environment

  • LonMaker 3.X
  • TAC Vista System Plug-in

Cause

There are two types of credits: Product specific credits like LonMaker or NL credits and then there are LNS credits. LonMaker/NL credits are used by LonMaker/NL220 to commission devices. LNS credits are not consumed by commissioning devices in LonMaker, but are consumed when commissioning devices in NL220. LNS credits are used by other LNS applications – like the TAC Vista System Plug-in. While LNS credits may not be consumed by LonMaker, they must be present in order for the plug-ins to launch. Backing up, sharing, and restoring LNS databases can sometimes corrupt these LNS credits, which then prohibits you from launching any LNS plug-ins. For more information regarding NL220 and LNS credits see Ordering more LNS credits.

Resolution

Echelon released a Licensing Update in January of 2006 to improve the reliability of the Echelon licensing software, which was compromised due to newer security and self-protection features of Windows. This will not fix your already corrupted license files; however, this will help prevent the license from becoming corrupted in the future. It is highly recommended that this update be installed on all applicable products. 

  1. If you do not already have the LNS Licensing Update 2006 software (LnsLicensingUpdate2006.exe), download it from http://www.echelon.com/support/downloads/detail.asp?partNum=153-0155-01A. If you do not already have one, you will need to create a user account with Echelon. It is free.
  2. Shut down all LNS applications, including LNS enabled Windows services. LNS enabled Windows services are LNS applications that are being run under the Windows Service Manager as background processes. Examples from Echelon include the LNS Server application and the LNS DDE Server. Third party examples are typically HMI drivers for HMI workstation software products.
  3. Log on with Administrator privilege.
  4. For version 3 LNS Server installations that are not already at LNS version 3.08 or higher, LNS 3 Service Pack 8 or higher must be installed before applying this update. Service packs are available from www.echelon.com/downloads.
  5. Run LnsLicensingUpdate2006.exe.
  6. Reboot if requested by the installer.

To resolve the issue of corrupted LNS credits:
 

LNSServerLicenseWizard.png

 

OrderNewLNSCredits.png

 

  1. Run the LNS Server License Wizard by navigating to Start > Programs > Echelon LNS Utilities > LNS Server License Wizard. It can also be found at C:\LonWorks\bin\LnsLic.exe.
  2. If the Max Credits, Credits Available, Max Deficits, Deficits Remaining, or Days Remaining are displaying zero values, then your LNS credits have become corrupted.
  3. To order free LNS replacement credits, hit Next.
  4. Hit Copy to Clipboard and paste into a blank email.
  5. After entering your specific contact information, you will want to check the "No Charge" box and the "Replacement Use" box.
  6. Before you send the form via fax or email, you also need to provide evidence that your LNS credits have been corrupted. Select Start > Run > and type "cmd" to reach a command prompt. This command will check the status of the LNS credits:

    checklic nsseng.exe

    An example of a working license is show below:
    checklic.png

     

  7. The output of this command should either be printed and sent with the fax or included in the email.
  8. Send the completed form to credits@echelon.com or print the forms and fax them to 1-408-790-3833. Note: If you are accustomed to ordering credits through another entity, do not send them this form. Only Echelon can issue replacement LNS credits.
  9. Echelon will reply with an application key that can be entered in this same window. When the LNS credits are restored, the System Plug-in should launch.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 3895
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore