Error: lc_checkout failed: Feature has expired.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Error: lc_checkout failed: Feature has expired.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • LeeCravens
    LeeCravens
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2473 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Error: lc_checkout failed: Feature has expired.

Picard Product_Support
‎2018-09-06 01:34 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:41 AM

Issue

When starting Vista software (other than Vista Server) an error appears stating that the license has expired.

lc_checkout failed: Feature has expired.
Feature: Menta.View
Expire date: 31-May-2011
License path: C:\Program Files\Schneider Electric\License Files\Demo_5_1_31_may_2011.lic
FLEXnet Licensing error:-10,32
For further information, refer to the FLEXnet Licensing documentation, available at "acresso.com".

Product Line

TAC Vista

Environment

  • Vista Workstation
  • Menta
  • TGML Editor
  • Vista Webstation

Cause

The temporary trial license for Vista has an expiration. If Vista returns an error stating that the license is expired this may be due to one or more of the following reasons:

  1. The temporary license file being used has indeed expired
  2. Vista was pointed to a temporary license file that has now expired rather than being pointed to the license files folder
  3. The computer date is set incorrectly

Resolution

  1. Start by checking to see that the computer date is set correctly. If it is set to a future date beyond the expiration date of the temporary license file this will prevent Vista from starting up.
  2. Check to verify that the temporary license file being used has not expired by opening Windows Explorer and browsing to the following folder:

    C:\Program Files\Schneider Electric\License Files or

    C:\Program Files\TAC\License Files if this is an older installation.

    The expiration date of the file is part of name of the file. For example, Demo_5_1_31_aug_2011 expires on the 31st of August, 2011. The terminal services licenses need to be updated every two weeks and the expiration date can also be found in the file name in a week-of-the-year format. The easiest way to find the exact date is to open the license file in a text editor  and the expiration date can be found in the first line. For example, the first line of the license file Demo+TS_OK_5_1_valid_through_week32_2011 is: "FEATURE Vista.Workstation taclic 5.1 14-aug-2011 uncounted \" therefore this license expires on the 14th of August 2011.

  3. If the exact license file rather than the license location was specified during installation, Vista may not be able to find a new temporary license file once the old one expires. The location where Vista looks for the license should be cleared out by following the steps in the resolution of Switching from the Demo license to the site License in Vista 5.1.7 or older. Once the registry value has been cleared Vista will ask where the license is found the next time it is started up.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5742
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore