Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

EcoStruxure Building Operation - Binding to a Graphic, what is the correct method?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • EcoStruxure Building Operation - Binding to a Graphic, what is the correct method?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • SharlinaRe
    SharlinaRe
  • sesa139513
    sesa139513
  • DavidFisher
    DavidFisher
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4039 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EcoStruxure Building Operation - Binding to a Graphic, what is the correct method?

Picard Product_Support
‎2018-09-06 10:48 AM

Last Updated: Administrator CraigEl Administrator ‎2023-05-11 05:31 PM

Issue

Binding to a Graphic, what is the correct method?

Product Line

EcoStruxure Building Operation

Environment

  • Bindings
  • Graphics

Cause

In the chapter "Binding Templates - Binding Values Using a Binding Template" in the "EcoStruxure Building Operation - Technical Reference Guide" it states "When creating bindings, follow the recommended general guidelines: create binding between Inputs and Outputs only, and do not create binding to Public Signals".
Does that mean that you should not bind constants used in e.g. curve block or time delays or outputs from expression blocks to a graphic?

Does that mean that you should not bind constants used in e.g. curve block or time delays or outputs from expression blocks to a graphic?

Resolution

Bindings from public signals to graphics is appropriate.

When dealing with directional bindings (i.e. in from a schedule, out to an alarm, in from or out to another program, etc.), it's best to bind to input blocks or output blocks.  Graphics bindings are a different animal, though.  Among other things, they are bi-directional and only affect the system when the graphic is displayed.  They also exist to give the user access and control to values throughout the system (rather than to control routine data flow).

Our primary reason for communicating this best practice is to help with the binding process.  Programs will operate with un-bound points, but we're encouraging users to simplify the binding process by relying on just inputs and outputs to interconnect a program with other logic and alarms.  In this way, you can visually scan the list of inputs and outputs to see which points still need to be bound. Since most programs typically have a much longer list of public signals, it's easier to overlook a missed public signal binding. Missed graphics bindings should be easier to catch but bindings to another program or alarm may be difficult to identify.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 12058
  • SharlinaRenwall23
Was this article helpful? Yes No
34% helpful (1/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore