Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

ETL Task not working when running as a service

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • ETL Task not working when running as a service
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • Benji
    Benji
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3448 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

ETL Task not working when running as a service

Picard Product_Support
‎2018-09-11 08:15 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-05-09 08:28 AM

Issue

When creating an ETL task the "Run Once" option works, but when configured to run as a service, it doesn't work and an error occurs in the error log:

2015-05-22 17:13:59,069 ERROR ETLEngine (TaskName) - Thread ID (119) - Power Monitoring Expert Load Task: Task Power Monitoring Expert Load Task failed
System.ApplicationException: Failed to populate the MetaDataSet. ---> System.Data.SqlClient.SqlException: Cannot open database "ION_Data" requested by the login. The login failed.
Login failed for user 'NT AUTHORITY\SYSTEM'.

Product Line

EcoStruxure Building Operation, Other

Environment

  • Power Monitoring Expert
  • Energy Expert (formerly Power Manager)
  • ETL Tool

Cause

  • When testing the ETL task using "Run Once", the Windows account currently logged in, will be used to access the SQL database. However, when the same Task is then configured to run as a service, the account configured on that Service will be used to access the SQL database instead.  By default that account is the built-in account 'NT AUTHORITY\SYSTEM'.
     
  • The Position values for all of the mapped trend logs are set to an unreasonable timestamp. The timestamp is either very old or a date the preceeds the oldest values in the database. 

Resolution

Changing the Windows system account for the ETL service

  • Either give the system account access to the database, or change the account used to run the service.

Correct/Adjust the timestamp values in Positions tab of ETL

  • The timestamps can be changed all at once by setting the Initial value field at the top of the "Positions" window in the ETL tool. 
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • 17959
  • DavidKendrick23
  • job
  • pm
  • pme
Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore