Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

EBO Server backup process fails

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • EBO Server backup process fails
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • JohnBoehmer
    JohnBoehmer
  • Reza
    Reza

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2498 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EBO Server backup process fails

JohnBoehmer Schneider Alumni (Retired)
‎2022-02-09 08:58 AM

Last Updated: Lt. Commander Reza Lt. Commander ‎2022-08-19 06:20 AM

Issue

Unable to back up the Automation Server

Unable to retrieve a working backup from an Automation Server

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Automation Server
  • Building Operation Automation Server Premium
  • Building Operation Enterprise Server
  • Building Operation Enterprise Central

Cause

Corrupt configuration.db

Network environment issues

Power failure

Resolution

Database Corruption

When the server backup process is initiated, the server tests the integrity of the configuration.db.  If the database does not pass the integrity test, the backup process is terminated, and no resulting backup is produced.

In this case, an older backup will need to be used.  The backup should be bench tested for integrity before restoring to the production server.

 

Network Environment

In some cases, the AS may produce a valid backup file, but when the backup is saved off of the server the file size is unusually small.  This can happen when network issues interfere with the backup save to disk process.  

In such cases, Automation Server backups taken from the Enterprise server will usually be damaged as well. 

 

You can work around this problem by connecting a Workstation laptop PC directly to the AS with an ethernet cable, thus eliminating the network from the process.

Backups can also be retrieved in this way using most versions of Device Administrator. 

 

Power Failure

The power fails while the EcoStruxure BMS server is backing up and the system displays a “Failed backup” message in the Event view. The solution is to initiate a new backup when the power resumes and the EcoStruxure BMS server goes back online. Power Failure Occurs During Backup 
 

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • JohnBoehmer22
  • RezaAmirzadeh22
Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore