EBO Script RESTful Web Services Basic Authentication

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • EBO Script RESTful Web Services Basic Authentication
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
3339 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EBO Script RESTful Web Services Basic Authentication

Kirk Mahmoud_Sayed Kirk
‎2022-08-01 10:35 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:55 AM

Issue

How to add Basic Authentication header to SendWebRequest function in Script RESTful Web Services

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Enterprise Central
  • Building Operation Automation Server
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled

Cause

A 3rd party web service requires basic authentication for HTTP requests to ensure that data is requested securely, otherwise, the request will be rejected with an "Authorization Error".

 

Resolution

Basic Authentication is a type of Authorization Request Headers, which transmits credentials as user-id/
password pairs, encoded using Base64, as defined in RFC 7617 - The 'Basic' HTTP Authentication Scheme (ietf.org). 

Follow the below steps to create a Basic Authentication header in Script RESTful Web Services:

  1. Combine the User ID and the Password with a colon ex. "aladdin:opensesame".
  2. Encode the resulting string in base64 using script function to base64 encode a string posted in the Community or using the online encoder as Base64 Encode and Decode - Online, ex.  "aladdin:opensesame" will be "YWxhZGRpbjpvcGVuc2VzYW1l" after Base64 encoding.
  3. Construct SendWebRequest header in the following format: 

Authorization: Basic <credentials>, as below example: 

Headers= "Authorization: Basic YWxhZGRpbjpvcGVuc2VzYW1l"'User ID=alaadin Password=opensesame
Resultstring= SendWebRequest(BaseUrl,Method,ContentType,Headers,Message)

Note: Basic Authentication is not a secure method of user authentication unless used in conjunction with HTTPS/TLS, as the user ID and password are transmitted as clear text. User ID and Password are Base64 encoded but Base64 can be easily decoded. 

For more information refer to Script RESTful Web Services WebHelp and Authorization - HTTP | MDN (mozilla.org)

Labels (2)
Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • MahmoudSayed22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore