Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Duplicate UID in a Vista Master / Slave (noded) network

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Duplicate UID in a Vista Master / Slave (noded) network
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Sacco
    Sacco
  • sesa150561
    sesa150561
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1589 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Duplicate UID in a Vista Master / Slave (noded) network

Picard Product_Support
‎2018-09-07 04:30 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:15 PM

Issue

The B0cfglog.txt file located in the Vista database $log folder and Alarms in Vista are getting the error:

Physical unit "Unit Name" on node "Node Name" is a duplicate by uid=### with "Unit Name" on node "Node Name"

Product Line

TAC Vista

Environment

  • Noded Vista Server
  • Master / Slave Vista

Cause

Conflicting UID in a Master/Slave node network.

Master Vista Server or Master. In a Vista network/system containing several Vista Servers, one of the Vista Servers is the Master Vista Server, managing and communicating system-specific information and global settings throughout the Vista network/system.

Slave Vista Server or Slave. The Slave Vista Servers in a Vista system receive system-specific information and global settings from the Master in the Vista network/system.

If once standalone servers are all added to one Master network, the Master assigns a unique ID to each slave. Normally when a UID gets duplicated the master tells the servers correct the duplication. Sometimes this automated fix cannot occur because the duplication prevents the proper communication.

In this case, the slaves need to re-establish communication with each other and be restarted.

Resolution

  1. Delete the slaved node
  2. Update Vista to reflect the node is removed
  3. Adding the node back
  4. Restart Vista Server

The UID should be resolved and the error should not be present.  If the error still comes up please try the following steps:

  1. Make current backups of all Vista Databases
  2. Close the slave server
  3. Open the mater server
  4. When asked, "Do you want to change identities on this node?" select Yes
  5. Close the master server and reopen both the mater and the salve server and the error should be gone

Instructions on how to add the Vista Slave node onto the master can be found in Creating TAC Vista multi-server network.

For this to work, the slaves need to be able to see each other as well. If you do not want the slaves to see each other, add them while balancing the load on the network. They can later be removed when the problem is not occurring anymore. 

Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4456
  • multi-server
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of