Door Controller Capacity

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Door Controller Capacity
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Roger_Bently
    Roger_Bently
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1912 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Door Controller Capacity

Picard Product_Support
‎2018-09-06 01:17 PM

Last Updated: Picard RobertAndriolo Picard ‎2021-09-15 05:02 PM

Issue

  • Number of individuals that a controller can have based on the firmware revision.
  • Adding individuals to a system that has more than 24,000 users and is not working.

Product Line

TAC INET

Environment

  • I/NET Seven
  • DPU 7910
  • DPU 7920 with or without 48K MIP Card
  • SCU1284

Cause

Although TAC I/NET supports up to 32,000 individuals per tenant, the model type and revision date of a tenant’s door controllers will ultimately determine how many individuals will be supported

Resolution

I/NET Supports up to 32,000 individuals per tenant based on the model type and revision date of the tenant's door controllers determines how many individuals it will support. The following table shows the capacity of the various door controllers.

Firmware Revision Door Controller Maximum Number of Individuals Maximum number per Tenant
2.1X and earlier DPU 7910, DPU 7920 Up to 24,000 per door 24,000
2.2X to 3.23

DPU 7910, DPU 7920 w/o 48K MIP

Up to 48,000 per controller.

24,000

DPU 7920 with 48K MIP, SCU 1284

Up to 48,000 per door1

3.24 and later DPU 7920 with 48K MIP, SCU 1284 Up to 64,000 per door1 32,000

1Typically, the total number of individuals for a selected door cannot exceed 32,000. However, if one of the two doors controlled by a DPU is not being used (that is, no individuals are assigned to the door), you can assign up to 64,000 individuals to the door that is being used. This also requires the use of more than one tenant since no single tenant can have more than 32,000 individuals.

Labels (1)
Labels:
  • TAC INET
Tags (4)
  • Find more articles tagged with:
  • 6178
  • HernanUruena23
  • RobertAndriolo19
  • RobertAndriolo21
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore