Do NOT use Backup and Restore to duplicate Automation Server databases! (1.5 and below).

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Do NOT use Backup and Restore to duplicate Automation Server databases! (1.5 and below).
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • DavidFisher
    DavidFisher
  • Benji
    Benji
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2922 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Do NOT use Backup and Restore to duplicate Automation Server databases! (1.5 and below).

Picard Product_Support
‎2018-09-11 06:04 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2022-08-21 05:36 AM

Issue

It has come to our attention that people are using Backup and Restore to duplicate Automation Server databases, this is not supported and should not be used as it results in various issues.  Some of the known issues at this time are listed below:

  • When attempting to update Server IP addresses using the advanced feature "Repair server communication"; one or more Automation Servers are listed as Offline even though they are shown as Online within the System Tree.
    (Click on image for larger view)
    Click for larger viiew

     
  • When performing a backup / restore from the Enterprise Server the Automation Server(s) are not listed as part of the Child view. 
    Click for larger view
     
  • Right-clicking on the Automation Server does not give all the options available and most are grayed out.
    Click for larger view

Product Line

EcoStruxure Building Operation

Environment

Building Operation Automation Server 1.2, 1.3, 1.4 and 1.5

Cause

This situation arises because each Automation Server receives a unique identifier, global unique identifier (GUID), when using the backup and restore function this GUID is retained.  Therefore when restored to other Automation Servers these will retain the same identifier.  The only course of action available within this environment is to detach the Automation Server from the Enterprise Server and create a new database from scratch. The correct duplication process across Automation Servers is to use the export and import feature or copy and paste (drag and drop) across Automation Servers.  

Resolution

StruxureWare Building Operation 1.6 and above update:  

You can now use the Restore function to re-use the configuration data from a backup set in a new standalone Automation Server. Rather than manually configuring your preferred Automation Server configuration, you can save time and configure the standalone Automation Server from a backup set.

Online help topic: Duplicating an Automation Server Using Restore


Backup and Restore feature should NOT be used to duplicate multiple Automation Server's databases it should only be backed up and restored to the same server.  Instead the Export / Import and copy and past features are designed for this function.   A warning note in the Technical Reference and IT Reference guides (versions 1.2, 1.3, & 1.4) has been added warning the users not to use the backup and restore function for duplication.  See the online StruxureWare WebHelp for this current Important Note (login required):

Backup and Restore Overview

However if you have this situation then it may be possible to recover some or most of the database, please contact Product Support and reference this article number so that this issue can be confirmed.  

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Tags (4)
  • Find more articles tagged with:
  • 12745
  • 12762
  • attach
  • MahmoudSayed22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore