Displaying Automation Server status on a graphic page

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Displaying Automation Server status on a graphic page
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Gary
    Gary
  • RyanSuar
    RyanSuar
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3511 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Displaying Automation Server status on a graphic page

Picard Product_Support
‎2018-09-11 12:54 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-22 07:46 PM

Issue

Displaying Automation Server status on a graphic page

Product Line

EcoStruxure Building Operation

Environment

Building Operation Workstation

Building Operation Webstation

Automation Server

Cause

The online / offline status of an Automation Server can be viewed in the Workstation System Tree (Servers folder). However, there is currently no 'built in' method of displaying the Automation Server status on a graphic page. 

Resolution

There are two possible ways to workaround this

 

Within TGML

Bind any Automation Server attribute that is shown only when the Automation Server is online (such as DateTime) and convert the status either by TGML script or a ConvertStatus element. See the attached example.

 

Using a script program

We can create a point in the Automation Server and use another server to monitor this point. Below is an example of using the Enterprise Server to monitor an Automation Server. 

Create a value point in the Automation Server. In this example, I have created an Analog Value
point and set it to a value of 88.8. This value does not really matter but I have set to this value
for easier recognition.
Create a value point in the Automation Server. In this example, I have created an Analog Value
point and set it to a value of 88.8. This value does not really matter but I have set to this value
for easier recognition

1. Create a value point in the Automation Server. In this example, an Analog Value point (named 'Status')is created and set to a value of 88.8. The value set does not matter. It has been set to 88.8 for easy recognition. 

 

2. In the Enterprise Server, create a new Program point (named 'Monitor AS' in this example) with the following codes. 

Numeric Input In1
String Output Out1
Numeric Output Out2

Out2 = In1

If In1.Offline = true then Out1 = "Offline" else Out1 = "Online"

 

3. Edit the binding of the Script program and bind 'In1' to the Value Point that was created in the Automation Server. 

 

4. When the Automation Server loses connectivity to the Enterprise Server, the Out1 output of the Script program will show 'Offline'. You can then bind this to a graphic page.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
StatusExample.zip
Tags (4)
  • Find more articles tagged with:
  • 12692
  • CraigEllis22
  • GaryMontague22
  • Not Working EBO 2022
Was this article helpful? Yes No
40% helpful (2/5)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore