Issue
Display the Text Value for a multistate point (e.g. enumerated SNVT) instead of the numerical value in a TAC Vista Graphic page.
Product Line
TAC Vista
Environment
- Vista IV
- OGC Graphics Editor
Cause
A digital presentation will display the integer value of the enumerated SNVT by default (1, 2, 3...). Many structured SNVT types use default enumerations (e.g. HVAC_HEAT, HVAC_COOL, HVAC_OFF). Rather than setting up a customer dynamic text value each time, the standard enumerations can be displayed.
Resolution
- Add a digital presentation to the Graphic page
- Browse in multistate point.
- Check the check box "Presentation format." Now the text will be displayed instead on the numerical value.
To define custom texts for use with multiple points, see Creating custom Multi-state Text definitions.