Discovering Lon Devices in SmartStruxure
  • Discovering Lon Devices in SmartStruxure
‎2018-09-11 02:56 PM
Last Updated: Crewman ContentModerator ‎2025-08-11 03:54 AM
How to discover MNL Lon devices or other Lon devices in an SmartStruxure Automation Server.
  • Building Operation Workstation
  • Building Operation Automation Server
Use the below instructions when you need to find all Lon devices on a Lon network.
To discover a LonWorks device
  1. In WorkStation, in the System Tree pane, select the server that is connected to the device you want to discover.
  2. Click the Device Discovery view.
  3. In the Select device type box, select LonWorks.
  4. Select the Devices folder.
  5. Right click on the Devices folder and take "Scan network for devices"
  6. In the Device Discovery view, ensure that the LonWorks device is displayed in the Devices folder. This may take up to 5 seconds.
  7. Drag the discovered device to the System Tree pane:
    • Drag to an existing device to associate it with the discovered physical device.
    • Drag to the LonWorks network to create the device.
NOTE: You cannot drag a standard MNL LonWorks device to the System Tree pane if the discovered device is in an unconfigured state
For more information, refer to the Creating and Configuring a LonWorks Network with MNL LonWorks Devices [102423].pdf document