Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Different options on the CyberStation security key

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Different options on the CyberStation security key
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • sesa139513
    sesa139513
  • PaulFr
    PaulFr
  • Alan_Wood
    Alan_Wood
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3228 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Different options on the CyberStation security key

Picard Product_Support
‎2018-09-06 12:26 PM

Issue

What are the different options on the CyberStation security key?

Product Line

Andover Continuum, Pelco

Environment

CyberStation

Cause

Documentation

Resolution

NOTE: These are the options used to program a security key but not necessarily what shows when a key is read using MMC key reader.

For example when a key is programmed for FIPS-201 it does NOT show the -F when the key information is read using MMC key reader, one way to know if FIPS-201 is enabled is to look at the Allowed Credentials setting in the Cyberstation, the FIPS credential options will be blank if the Cyberstation key is not enabled for FIPS-201

CyberStation:

SU-INT           Single User Integrated

SU-HVAC      Single User HVAC

SU-SEC        Single User Security

LAN-INT        LAN Integrated

LAN-HVAC   LAN HVAC

LAN-SEC      LAN Security

 

CyberStation Options:

-U                    Unlimited Points

-P                    Programmer’s Version

-B                    Badging Option

-CFRB1           Basic CFR Compliance Pack – 1st Workstation

-CFRBV1        Basic CFR Compliance Pack – 2nd Workstation & up

-CFRA1           Advanced CFR Compliance Pack – 1st Workstation

-CFRAV1        Advanced CFR Compliance Pack – 2nd Workstation & up

-D                    Data Exchange Option – includes Personnel Import Utility

-E2, 3                Endura integration option

-F1, 2                FIPS 201 option

-USB4             USB Key

 

1    Option requires special approval before it can be enabled.

2    Option only available through software upgrade process; cannot be ordered with new P/N configurations.

3    New option introduced in v1.91; required per workstation for integration with a Pelco Endura system. Currently this is free as of 8/2/14 but needs a cookie       from repair for this option to work

4    USB Key Option is mandatory for new orders

Note: The Continuum version number of a key, allows it to operate with all Cyberstation versions up to that release.

Labels (2)
Labels:
  • Andover Continuum
  • CCTV
Tags (1)
  • Find more articles tagged with:
  • 7776
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore