Different options for EBO to serve data to 3rd party systems

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Different options for EBO to serve data to 3rd party systems
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
5 Likes
8818 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Different options for EBO to serve data to 3rd party systems

Kirk Mahmoud_Sayed Kirk
‎2021-12-12 05:42 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:55 AM

Issue

How can EcoStruxure BMS server serve data to external devices or software?

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Enterprise Central
  • Building Operation Automation Server
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled
  • Building Operation Edge Server - Standard
  • Third party devices or software

Cause

The EcoStruxure Building Operation software supports the major communication protocols in building automation and security management. In many projects, it is required that an EcoStruxure BMS server serve data to external devices or software, E.X. HMI, SCADA or power monitoring.

Resolution

The following is a summary of the available options to serve EcoStruxure BMS server data to the external world:

  1. BACnet: 

    When you create a BACnet Interface, the system automatically creates the Application and IP network folders within the BACnet Interface folder on the System Tree. If you create a BACnet Interface for a SmartX server, you can optionally create an MS/TP network. You can create BACnet objects in BACnet application folder of EcoStruxure BMS servers and these object will be visible for external BACnet clients.

    More information about EBO BACnet interface: BACnet Interface

     
  2. Modbus Slave network: 

    If you configure the Modbus Slave Network (and associate it with a serial port), you can set up any external Modbus master device to communicate with the internal Modbus Interface. In this example, a Modbus Slave Network is set up on an EcoStruxure BMS Server and the external master device is configured with the same Modbus properties as the Modbus Slave Network object. The Modbus master device can also be an HMI device.

    More information about Modbus serial interface: Modbus Serial Networks

    Modbus Slave.png
  3. Modbus server network:

    You can create a Modbus TCP Network on an Ethernet network (TCP/IP).  You can create an internal interface which acts as the server to an external client/clients.

    More information about Modbus TCP interface: Client and Server Networks

    Modbus Server.png

     

  4. MQTT:

    MQTT is a lightweight and flexible data transfer protocol for IoT resources. EcoStruxure Building Operation, V3.2 or higher, can be configured to send data to an MQTT broker on interval or event-driven. The below are the tested brokers:

    • Microsoft Azure IoT Hub

    • Amazon IoT Core

    • IBM Watson IoT

    • Mosquitto

    More information about MQTT interface: MQTT Overview

    MQTT.png

  5. LonWorks Interface:

    EcoStruxure BMS servers can have a local node on their networks that can act as a LonWorks node. In the local node, you can create your own NVs that can be bound to external LonWorks devices using LonWorks bindings. The NVs in your local node can then be used in EcoStruxure Building Operation bindings for applications and graphics.

    More information about LonWorks interface: LonWorks Engineering

    LonWorks.png

     

  6. SNMP:

    Simple Network Management Protocol (SNMP) is an Internet-standard protocol for managing devices on IP networks. The EcoStruxure BMS servers support SNMP version 3. The SmartX servers support several SNMP traps. SNMP traps enable an agent to notify the management station of significant events by way of an unsolicited SNMP message.

    More information about SNMP: SNMP

    SNMP.png
  7. EcoStruxure Web Service (EWS) server:

    EcoStruxure Web Services allows seamless sharing of operational data, including alarms and historical information, between software from different Schneider Electric Business Units. When the EcoStruxure BMS server is an EcoStruxure Web Service server, it exposes objects, such as values, to another EcoStruxure system that is an EcoStruxure Web Service client. The EcoStruxure Web Service client can read and change values on the EcoStruxure BMS depending on the configuration of the EcoStruxure BMS server.

    More information about EBO EWS Server: EcoStruxure Web Service Server

  8. Smart Connector:

    A development framework that simplifies and accelerates integrations with third-party systems or other data sources. It is an open, extensible and configurable application framework that allows developers to create innovative new capabilities, applications, and solutions which extend and enhance EcoStruxure Building solutions. Ex. SmartConnector can be used to serve EBO data in a RESTful manner, refer to: Configure SmartConnector RESTful EWS Gateway to serve EBO data

     

    Smart Connector.png

For further information watch the Smart Connector explainer video or visit the Smart Connector Developer Community on the Exchange:

For developers wanting to get started using the Smart Connector framework visit:
https://www.smartconnectorserver.com

Smart Connector at Exchange: 

EcoStruxure Building Operations SmartConnector 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • ddc
  • MahmoudSayed21
  • MahmoudSayed25
  • StephenYang25
Was this article helpful? Yes No
100% helpful (8/8)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore