Determining Air Flow in Cubic Feet per Minute (CFM)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Determining Air Flow in Cubic Feet per Minute (CFM)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood
  • DavidFisher
    DavidFisher
  • sesa194431
    sesa194431
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4325 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Determining Air Flow in Cubic Feet per Minute (CFM)

Picard Product_Support
‎2018-09-10 07:56 AM

Last Updated: Administrator CraigEl Administrator ‎2023-07-12 05:43 PM

Issue

Converting the Velocity Pressure measured by the pressure sensor to Flow velocity (CFM)

Product Line

Andover Continuum,TAC INET,TAC Vista

Environment

Air flow measurement / balancing

Cause

Requirement for converting the velocity pressure to flow velocity (CFM)

Resolution

To calculate Air Flow in Cubic Feet per Minute (CFM), determine the Flow Velocity in feet per minute, then multiply this figure by the Duct Cross Sectional Area.
Air Flow in CFM (Q) = Flow Velocity in Feet Per Minute (V) x Duct Cross Sectional Area (A)

 

Determining Flow Velocity

The easiest way to determine Flow Velocity is to measure the Velocity Pressure in the duct with a Pitot Tube Assembly connected to a differential pressure sensor. The Pitot Tube Assembly includes a Static Pressure Probe and a Total Pressure Probe. A Total Pressure Probe, aligned into the airflow, senses the duct velocity pressure and the static pressure, which equals the total pressure. A Static Pressure Probe aligned at a right angle to the airflow senses only the static pressure. The difference between the total pressure reading and the static pressure reading is the Velocity Pressure. If you connect the Total Pressure Probe to the HIGH port on a differential pressure sensor and the Static Pressure Probe to the LOW port on the differential pressure sensor, then the sensor’s output will be the Velocity Pressure, as shown in the figures below.

The Flow Velocity is then determined with the following equation:
V = 4005 x Sqrt(ΔP)
V = Flow Velocity in feet per minute.
Sqrt() = Square root of the number in the parenthesis.
ΔP = The Velocity Pressure measured by the pressure sensor
Example: Measuring a Velocity Pressure of .75” W.C. equals a Flow Velocity of 3,468 Ft/Min.
V = 4005 x Sqrt(0.75)
Sqrt(0.75) = 0.866 • 4005 x 0.866 = 3,468 • Flow Velocity = 3,468 Ft/Min

 

Determining Duct Cross Sectional Area

After obtaining the Flow Velocity from the previous procedure, that figure is now multiplied by the Duct Cross Sectional Area to determine the Air Flow in CFM.
There are two different equations for determining the Duct Cross Sectional Area, one for round ducts and one for square or rectangular ducts.
The equation for a round duct is:
A = π x r2
A = Duct Cross Sectional Area
π = 3.14159
r = radius of duct in feet

The equation for square or rectangular ducts is:
A = X x Y
A = Duct Cross Sectional Area
X = Duct height in feet
Y = Duct width in feet.
Example: An 18” diameter round duct has a Duct Cross Sectional Area of 1.77 Ft2
A = π x r2 or A = 3.14158 x .5625
18” diameter is 1.5 feet, therefore the radius is .75 feet • r2 = 0.752 = 0.5265 • π = 3.14159
A = 3.14159 x 0.5625 = 1.77 Ft2

 

Determining Air Flow in CFM

After obtaining the Flow Velocity and the Duct Cross Sectional Area from the previous two procedures, the Air Flow in CFM is determined by multiplying the two:
Air Flow in CFM (Q) = Flow Velocity in Feet Per Minute (V) x Duct Cross Sectional Area (A)

Example
An 18” diameter round duct with a Velocity Pressure of .75” W.C. has an Air Flow of 6,128 CFM
The Flow Velocity is 3,468 Ft/Min.

V = 4005 x Sqrt(ΔP)
V = 4005 x Sqrt(0.75)
Sqrt(0.75) = 0.866 • 4005 x 0.866 = 3,468 • Flow Velocity = 3,468 Ft/Min
The Duct Cross Sectional Area is 1.65 Ft2
A = π x r2
π = 3.14159 • r2 = 0.752 = 0.5625
Duct Cross Sectional Area (A) = 3.14159 x 0.5625 = 1.77 Ft2
The Air Flow in CFM is 6,128 Ft3/Min
Air Flow in CFM (Q) = Flow Velocity in Feet Per Minute (V) x Duct Cross Sectional Area (A)
Air Flow in CFM (Q) = 3,468 Ft/Min x 1.77 Ft2 = 6,128 CFM

Labels (3)
Labels:
  • Andover Continuum
  • TAC INET
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 8070
  • AlanWood23
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore