Deleting a point from an MNB controller in StruxureWare Building Operation
  • Deleting a point from an MNB controller in StruxureWare Building Operation
  • RyanSuar
    RyanSuar
  • RobertAndriolo
    RobertAndriolo
‎2018-09-11 07:42 AM
Deleting a point from an MNB controller in StruxureWare Building Operation results in the following error
StruxureWare Building Operation: All versions up to and including 1.5.x
I/A Series Micronet BACnet Controller
StruxureWare Building Operation does not support the deletion of points in the Application Folder of a MNB device.
To delete a point, disconnect the MNB controller from the network. Once StruxureWare Building Operation server is unable to communicate with the MNB device, it will allow the deletion of the point in the Application folder.
Take note that even though the point has been deleted from the AS Application folder, the point still exist in the MNB controller.
Tags (3)
  • 16157
  • sbo
  • workstation
100% helpful (1/1)