DCom or other error message seen when running CyberStation
  • DCom or other error message seen when running CyberStation
  • Alan_Wood
    Alan_Wood
  • Dave_Shore
    Dave_Shore
‎2018-09-06 01:45 PM
Last Updated: Administrator CraigEl Administrator ‎2025-08-29 04:58 AM
CyberStation displays a DCom or similar error message during operation.
  • Extended logging errors may appear.
  • CyberStation may show “Error connecting to database” yet continue running.
  • Alarms may not appear in the Active Alarm window.
Andover Continuum
Continuum
This issue typically arises from a PC-level fault or a CyberStation configuration error that prevents proper database connectivity. Potential causes include:
  • Hard disk or RAM failure
  • Corrupted CyberStation installation
  • Network or permission issues
Further investigation is recommended to determine the root cause.
To resolve the issue:
  1. Reinitialize the database
    • Ensure all CyberStations are shut down before proceeding.
    • For LAN installations, select “Server” mode.
    • For standalone setups, use “Stand Alone” mode.
  2. Reinitialize the workstation
    • Close CyberStation completely.
    • Restart the workstation and launch CyberStation to test connectivity.
Additional Notes
  • If the issue persists after reinitialization, consider checking system logs, hardware diagnostics, and reinstalling CyberStation.
  • Contact Schneider Electric support for deeper troubleshooting if needed.
Tags (2)
  • 5306
  • AlanWood25