Cycling power 10 times does not clear Xenta controller application
  • Cycling power 10 times does not clear Xenta controller application
  • CraigEl
    CraigEl
‎2018-09-07 12:15 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:22 AM
Cycling power 10 times doesn't clear Xenta base units version 3.61 or later.
TAC Vista
Xenta Programmable Controllers rev 3.61 or later
A change to the firmware got rid of the 10 power cycles clearing the application.
To clear the memory of a Xenta 2xx/3xx/40x running system program 3.61 or later, i.e. clear out the Menta application, insert a reset plug into the RJ-45 serial connection and then give the controller power. If you don't already have one, it is quite simple to make. See How to Clear the Xenta Application for instructions on how to make a reset cable.