Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Creating a Custom Credential for an HID 37-Bit badge With No Site Code (H10302)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Creating a Custom Credential for an HID 37-Bit badge With No Site Code (H10302)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Brian_Feick
    Brian_Feick
  • David_Kendrick
    David_Kendrick
  • GavinHe
    GavinHe
  • JonGreen
    JonGreen
  • DavidChild
    DavidChild

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2769 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Creating a Custom Credential for an HID 37-Bit badge With No Site Code (H10302)

Ensign Brian_Feick Ensign
‎2021-03-15 12:59 PM

Last Updated: Sisko GavinHe Sisko ‎2023-03-06 01:38 AM

Issue

There is no built-in Credential Type for the HID 37-Bit badge with no site code (H10302).

Product Line

Security Expert

Environment

  • Security Expert Server
  • Access Card Format

Cause

Security Expert does not have the HID 37-Bit badge (H10302) with no site code as a built-in available Credential Type.

Resolution

1) In the Security Expert Client, select Sites -> Credential Types2021-03-15_15-15-34.gif

2) Create a new Credential Type with a name of your choosing.

3) Under Configuration, select the Format as Wiegand.

4) In the field labeled Wiegand or TLV Format, enter the following exactly as written:                                                        A,FACILITY,0,MSB,BIN__B,CARD,35,MSB,BIN__PBBBBBBBBBBBBBBBBBBBBBBBBBBBBBBBBBBBP_EXXXXXXXXXXXXXXXXXX.................._..................XXXXXXXXXXXXXXXXXXO

2021-03-15_15-16-20.gif

5) Save

 

NOTE:
This article assumes that the reader is familiar with creating and deploying Custom Credentials, If this is not the case, then please reference the Complex Transition Programming section of the Transitioning Continuum Sites to Security Expert - Transition Guide

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (3)
  • Find more articles tagged with:
  • BrianFeick21
  • DavidKendrick21
  • GavinHeward23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore