Creating a Counter input in b3 controllers.
  • Creating a Counter input in b3 controllers.
  • RobertAndriolo
    RobertAndriolo
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 09:57 AM
b3 controllers in StruxureWare Building Operation do not seem to support Counter inputs.
  • Counter Inputs
  • b3
SmartStruxure does support the creation of Counter inputs within b3 controllers.
Counter inputs are Analog Inputs.  When the Object Creation wizard is used to create an Analog input the user is prompted to select the electric type.  At this point select Counter.
  • 14761