Controllers with network security applied are not responding to a ping command after firmware upgrade
  • Controllers with network security applied are not responding to a ping command after firmware upgrade
  • GavinHe
    GavinHe
  • JohnBoehmer
    JohnBoehmer
  • Clifton_eakes
    Clifton_eakes
‎2018-09-06 07:36 AM
Last Updated: Sisko GavinHe Sisko ‎2023-05-16 08:34 AM
NC2 and ACX57xx controllers with network security applied will no longer respond to a ping command after upgrading to newest firmware.
Andover Continuum
  • Network Security
  • ACX5740
  • ACX5720
  • NC2
  • CX9680
The ping command was used to monitor controllers offline/online status.
CX9680 and ACX57xx controllers (with network security applied) stopped responding to  a ping command after respective firmware versions  v2.100048 and v1.100052 were applied.
This is functioning as designed due to the hardening of the controller's firmware for security reasons when network security has been applied.
Tags (4)
  • 19354
  • axc57xx
  • GavinHeward23
  • icmp