Need to interface Continuum system with 3rd party BACnet Ethernet devices on the network.
Continuum
BCX4040
Continuum with bCX BACnet IP devices need to share data with BACnet Ethernet device on the network.
Set one of the bCX on the network to be enabled for the BACnet Ethernet in bCX configuration webpage, and set the same value for the BACnet Network ID - Ethernet with the other Ethernet devices.
Enabling this option on a BCX allows the BCX to communicate both Bacnet IP AND Bacnet Ethernet, it does not turn off Bacnet IP.