Continuum SQL installation error due to BitLocker installed on machine

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Continuum SQL installation error due to BitLocker installed on machine
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JohnBoehmer
    JohnBoehmer
  • RobertAndriolo
    RobertAndriolo
  • JonGreen
    JonGreen

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2611 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Continuum SQL installation error due to BitLocker installed on machine

Commander JonGreen Commander
‎2019-06-27 09:47 AM

Last Updated: Picard RobertAndriolo Picard ‎2019-06-27 09:06 PM

Issue

During SQL install portion of Continuum installation the following error message is received.

"SQL Express is not installed properly. Please contact technical support representative."

F4BA6BA3.PNG

Product Line

Andover Continuum

Environment

  • Continuum Cyberstation (All Versions)
  • Microsoft SQL Express (Version dependent upon Continuum version)

Cause

Bit Locker has been installed on the system to which Continuum Cyberstation is being installed.

Bit Locker enforces specific password requirements across all Microsoft Windows products.

Find the SQL installation log at C:\Program Files (x86)\Microsoft SQL Server\110\Setup Bootstrap\Log\20190627_092341\Summary_WTUSLVSE076617L_20190627_092341.txt

*NOTE*

The parent folder of the log will include the date and time of the installation.

The log file name format will be Summary_(your computer name)_date_time.txt

At the bottom of the log, you will see an Exception summary which gives full detail of what the error is:

"Exception summary:
The following is an exception stack listing the exceptions in outermost to innermost order
Inner exceptions are being indented

Exception type: Microsoft.SqlServer.Chainer.Infrastructure.InputSettingValidationException
Message:
The specified sa password does not meet strong password requirements. For more information about strong password requirements, see "Database Engine Configuration - Account Provisioning" in Setup Help or in SQL Server 2012 Books Online.
HResult : 0x84b40000
FacilityCode : 1204 (4b4)
ErrorCode : 0 (0000)
Data:
SQL.Setup.FailureCategory = InputSettingValidationFailure
DisableWatson = true
Stack:
at Microsoft.SqlServer.Chainer.Infrastructure.InputSettingService.LogAllValidationErrorsAndThrowFirstOne(ValidationState vs)
at Microsoft.SqlServer.Configuration.SetupExtension.ValidateFeatureSettingsAction.ExecuteAction(String actionId)
at Microsoft.SqlServer.Chainer.Infrastructure.Action.Execute(String actionId, TextWriter errorStream)
at Microsoft.SqlServer.Setup.Chainer.Workflow.ActionInvocation.ExecuteActionHelper(TextWriter statusStream, ISequencedAction actionToRun, ServiceContainer context)
Inner exception type: Microsoft.SqlServer.Configuration.SqlEngine.ValidationException
Message:
The specified sa password does not meet strong password requirements. For more information about strong password requirements, see "Database Engine Configuration - Account Provisioning" in Setup Help or in SQL Server 2012 Books Online.
HResult : 0x851a0013
FacilityCode : 1306 (51a)
ErrorCode : 19 (0013)"

Resolution

Update or use password for new database that meets the minimum standards of:

  • 8 Characters
  • 1 Capital letter
  • 1 Numerical character
  • 1 Special character (!,@,#...)
  • 1 Lowercase letter

This will allow SQL Server to be installed

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • JonGreen19
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore