Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Continuum Reports Suite installation issues

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Continuum Reports Suite installation issues
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • sesa116095_brid
    sesa116095_brid
  • PaulFr
    PaulFr
  • Dave_Shore
    Dave_Shore

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2981 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Continuum Reports Suite installation issues

Picard Product_Support
‎2018-09-10 01:13 AM

Last Updated: Administrator CraigEl Administrator ‎2022-11-07 02:41 PM

Issue

Continuum Reports Suite installation issues. Example error message could be:

  • "Unrecoverable Error!"
  • "Alias 'CURRENT3' is not found"
  • "Method: ALARMEVENTS.RUN_REPORT_BTN.CLICK"

Product Line

Andover Continuum

Environment

Continuum Reports Suite

Cause

Problems with installing and running the Report Suite

Resolution

  1. When editing the "Continuum_Reports.dmp" file using Notepad.exe, WordWrap must be unchecked!  Unfortunately, opening "Continuum_Reports.dmp" and unchecking WordWrap is not enough!  When WordWrap is checked, you must uncheck and Exit Notepad.  Then Open "Continuum_Reports.dmp", edit and SAVE AS.  When WordWrap is enabled and changes are made, after you Save and reopen the file, you will notice that is corrupt and all the PE Codes is scrunched into one enormous line, instead of 550+ lines. Alternatively use a different editor, eg. Metapad or Notepad++
  2. If after editing and importing "Continuum_Reports.dmp", you discover there is no Plain English code or the Programs run, but are stuck on "Init", or other PE import / run issues, this is the result of incorrectly performing the Replacement of the workstation Folder Name.  When the Workstation Folder name and Workstation Name is correctly replaced, the PE programs will import and run properly.
  3. After installing Continuum Reports, you should confirm that the installation directory, "C:\Program Files\Continuum_Reports" has Modify privilege enabled for all "Workstation Users".
  4. After a Continuum Reports run-time error, run the Windows Task Manager and confirm that the "Reports.exe" Process does not exist.  If it exists, End the Process.
  5. If Continuum Reports does not exit normally, temp files will be orphaned in the C:\Program Files\Continuum_Reports\Data directory.  Although orphaned Temp Files do not affect Continuum Reports operation, they occupy disk space.  Temp files have an underscore ("_") as the first character.  To remove orphaned temp files, make sure Reports.exe is not running and CAREFULLY delete those files that have an underscore ("_") as the first character.
  6. Continuum Reports needs to be installed using the Setup Application. The Setup Application needs to be run on every workstation and configuration administered locally.
  7. Before you install Continuum Reports, the current version must be uninstalled.  Typically, uninstalling and reinstalling doesn't solve any problems.  But when this is done, make sure to delete the directory C:\Program Files\Continuum_Reports\DATA before reinstalling Continuum Reports.
  8. Continuum Reports remembers the Continuum Database access parameters, including Server Name, SQL Username and Password.  After installing Continuum Reports, you will need to run "Reset_Password.bat" if the Continuum Database name is not "ContinuumDB", or if appears that Continuum Reports is not accessing the correct database.
  9. If the Multi-Facility Report Data Partitioning has been used (17.2e onwards) the Revision Level in the upper right hand corner of the window is Red.  This indicates that Restrictions were enabled.  Therefore the whole database may not be queried. See "Continuum Reports Multi-Facility Report Data Partitioning Administration Guide"
  10. It is worth setting a default printer even if one does not exist. (use a PDF printer) If the default printer gets set to say a card printer, it can affect the output of the reports suite
  11. See the link below for all software and guides, always read, as required
    • ReadMe.txt
    • Upgradedoc.txt
    • Continuum Reports Installation Guide Rev x.x.pdf
    • @ Upgrade - Installation Instructions.pdf
    • https://ecoxpert.se.com/search#keyword/Coe/tab/documents
    • If you have other queries please contact COE.Support@Buildings.Schneider-Electric.com
Labels (1)
Labels:
  • Andover Continuum
Tags (7)
  • Find more articles tagged with:
  • 5529
  • add-on
  • add-ons
  • report suite
  • reporting
  • reports
  • suite
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore