Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Considerations for Sigma system controllers on multiple VLANs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Considerations for Sigma system controllers on multiple VLANs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1973 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Considerations for Sigma system controllers on multiple VLANs

Picard Product_Support
‎2018-09-07 07:40 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:32 PM

Issue

Can Sigma system controllers sit on multiple VLANs?

Product Line

Satchwell Sigma

Environment

  • Sigma all Ethernet controllers
  • Link Addressing

Cause

Question by IT departments before upgrading BAS to Sigma systems

Resolution

You can put Sigma controllers onto different VLANs. But there are considerations:

  1. Sigma global data to be passed between controllers on different VLAN's will require Link Addresses to be configured.
    This is because Sigma globals are transmitted using the Ethernet broadcast address. Typically, most broadcast address messages are blocked by the routers used to link/connect the VLANs. Hence Link Addressing is used to 'tunnel' through the VLAN routers.
  2. A DNN will have to be added to each sub-LAN for Link Addressing configuration.  For configuration details click Link Addressing.pdf.
  3. All Sigma devices (controllers, Servers and DNN's) will have to be configured with default gateway IP Addresses.
    • For controllers use pocket terminal command GW +  192.168.0.1  (where 192.168.0.1 is the default gateway for the local network)
    • For DNN's set a Static Route as defined in Having set Link Addressing in a Sigma DNN3 can no longer communicate to the DNN3 and Link Addressing....
    • For Sigma servers set the PC default gateway IP address via network settings - Internet Protocol (TCP/IP) - properties.

Therefore, although the answer is yes - Sigma controllers are supported on different VLANs, a 'flat' VLAN architecture is a simpler solution.

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
Tags (1)
  • Find more articles tagged with:
  • 4761
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of