Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Configuring Continuum Infinity Schedules to download across time zones.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configuring Continuum Infinity Schedules to download across time zones.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • BillNeville
    BillNeville
  • RobertAndriolo
    RobertAndriolo
  • LeeCravens
    LeeCravens
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1505 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring Continuum Infinity Schedules to download across time zones.

Picard Product_Support
‎2018-09-10 06:52 PM

Issue

Infinity schedules (as opposed to BACnet schedules) may not work correctly if downloaded to the controller before or after the current week of events ends.

Consider the scenario above, CX1 is located in LA (Pacific Time Zone) and CX2 is located in Boston (Eastern Time Zone), the Cyberstation performing schedule downloads is located in Dallas (Central Time Zone). If the schedules are configured with default download time of Sunday at midnight, CYBER1 will download the schedules to both CX1 and CX2 at (or shortly after) Sunday @ 12:00:00 Central time. Meanwhile, where CX1 is located in LA, the time is Saturday @ 10:00 PM and CX2, located in Boston, has a time of Sunday 1:00 AM

The controllers can only hold one week worth of events.

How a schedule download 2 hours ahead of time would affect the schedules in CX1?

 Any events in CX1 between 10:00 PM and midnight would be over written with events for the same period of the following week.

How a schedule download 1 hour late would affect the schedules in CX2?

On Saturday @ 11:59:59 PM Eastern time CX2 runs out of events for the past week. Since it has not yet received the events for the next week, it starts repeating the events in the schedule for the week that just ended.  If the schedule events for the week that has just started but not yet been downloaded to the controller happens to be the same as the previous week, in terms of events, then this does not present any problem. But if the two weeks differ in the events they have between Sunday midnight and 1:00:00 AM, the schedule will not function correctly.

IMPORTANT NOTE

It is important to note that the scenarios described in this article are only applicable if a schedule contains exceptions or happens to differ from week to week in terms of the events entered in the schedule.

If the schedule happens to be the same week after week, then it should not make a difference whether the controller receives a schedule download or not, from week to week. In fact, even if no download takes place at all, the schedule will function correctly as the controller will just repeat the same events week after week.

Also, BACnet schedules do not have this problem, when a BACnet schedule is created Continuum sends ALL of the events in the schedule to the controller instead of just one week worth of events as is the case with Infinity schedules.

Environment

Cyberstation

All Continuum controllers

Cause

Continuum Infinity Schedule download functionality does not automatically take into account time zone differences between Cyberstation and controllers.

Resolution

When configuring Infinity Schedules download day and time, it is very important to take into account the locale of the Cyberstation performing the download, as well as the locale of the controller receiving the downloaded schedules.

Configure the schedules' download time so that the download takes place on Sunday @ 12:00:00 AM IN THE TIME ZONE WHERE THE CONTROLLER IS LOCATED.

The schedules residing in CX1 in Los Angeles should be configured to download on Sunday @ 2:00:00 AM Central time which corresponds to Sunday @Anonymous user:00:00 AM Pacific time.

The schedules residing in CX2 in Boston should be configured to download on Saturday @ 11:00:00 PM Central time which corresponds to Sunday @Anonymous user:00:00 AM Eastern time. Note that the schedule download engine always downloads one week worth of events starting at the configured download time. In this case all events from Saturday @11:00:00 PM to the next Saturday @11:00:00 PM will be downloaded, which will ensure that CX2 never has to repeat any events from the previously downloaded week.

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 18325
  • infinityschedule
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of