Configure REX button to be able to permanently lock or unlock a door

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configure REX button to be able to permanently lock or unlock a door
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • JonGreen
    JonGreen
  • AdamSteele
    AdamSteele

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2684 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configure REX button to be able to permanently lock or unlock a door

Commander JonGreen Commander
‎2020-03-11 07:23 AM

Last Updated: Guinan AdamSteele Guinan ‎2024-11-26 08:56 PM

Issue

Configure REX button to be able to permanently lock or unlock a door if pressed for a set amount of seconds.

Product Line

EcoStruxure Security Expert

Environment

Security Expert Server

Cause

REX button does a momentary unlock then relatches the door. Would like to unlock or lock doors using the REX as determining factors are too dynamic to use a schedule.

Resolution

What is needed

  • 2 Inputs (A & B)
  • 4 Outputs (A, B, C, D, & E)
  • 4 Programmable Functions (A, B, C, & D)
  • 1 Dummy Area (Test Area)
  • 2 Input Types (Input Triggers Output & Input Toggles Output)
  • 1 Door with REX connected (Door X)

Inputs

    1. Input A (REX Button)
      1. General Tab
        1. Control Output: Output A
      2. Areas and Input Types Tab
        1. Area: Test Area
        2. Input Type: Input Triggers Output
    2. Input B
      1. General Tab
        1. Control Output: Output E
      2. Areas and Input Types tab
        1. Area: Test Area
        2. Input Type: Input Toggles Output

Input Types

    1. Input Triggers Output
      1. Options 1 Tab
        1. Generate Alarms checked
      2. Options 3 Tab
        1. Activate Input Control Output on Alarm checked
        2. Deactivate Input Control Output on Restore checked
      3. Input Toggles Output
        1. Options 1 Tab
          1. Generate Alarms checked
        2. Options 3 Tab
          1. Toggle Input Output State checked

Outputs

    1. Output A, B, C, and E are just standard virtual outputs
    2. Output D
      1. General Tab
        1. Activation Time (seconds): the amount of time you want to hold the REX to activate the unlock/lock (I.E. 5 seconds would require you hold the REX button for 5 seconds)

Programmable functions:

    1. Programmable Function A:
      1. Type: Ripple Output
      2. Output to trigger: Output A
      3. Stage 1: Output B
      4. Stage 2: Output C
      5. Inter Stage on Ripple Time: 5
    2. Programmable Function B:
      1. Type: Logic Control
      2. Logic Function Mode: 7 Follow Logic And
      3. First Output to Check: Output A
      4. Second Output to Check: Output C
      5. Output to Control: Output D
    3. Programmable Function C:
      1. Type: Input follows Output
      2. Input follows Output: Input B
      3. Output to follow: Output D
    4. Programmable Function D:
      1. Type: Door Control
      2. Door Function Mode: 0 Follow and Test Output
      3. Door control Mode: 1 Latch Door unlock
      4. Output to Check: Output E
      5. Door to Control: Door X

Make sure you right-click each programmable function and start them.

Go to the Test Area and set it to Armed.

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (2)
  • Find more articles tagged with:
  • AdamSteele24
  • JonGreen20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore