Issue
Product Line
TAC IA SeriesEnvironment
- I/A Series R2 UNC
- LonWorks Integration
Cause
Resolution
To Change Send Heartbeat (localLonDevice):
- Open the UNC station in WorkPlace Pro.
- Navigate to localLonDevice → Properties → Config tab.
- Adjust the following parameters:
- maxSendTime: Maximum time (in seconds) before sending an output value even if unchanged. Ensures periodic updates within the receiver’s heartbeat limit.
- minSendTime: Minimum time between updates to prevent network congestion from rapidly changing values.
To Change Receive Heartbeat:
- In the same Config tab, expand nvoStatusProps.
- Set Receive Heartbeat:
- If set to 0, the device does not expect periodic updates and only reacts to value changes.
- Use a non-zero value to enforce periodic updates for linked inputs.
Refer to Niagara LonWorks Integration Reference (pages 9-4 to 9-6) for detailed parameter definitions.