Issue
Clarify the hardware and software configuration required to integrate the Sigma Remote Alarm Manager (RAM) with a Multi-tone paging system using the ESPA 4.4.4 output driver.
Product Line
Satchwell BAS & SigmaEnvironment
- Sigma RAM
- ESPA 4.4.4 Driver
- Multi-tone Paging System
Cause
To enable communication between Sigma RAM and Multi-tone pagers, specific configuration steps and wiring are required for the ESPA 4.4.4 output driver.
Resolution
Driver Configuration
The ESPA 4.4.4 output driver enables Sigma RAM to send messages to the Multi-tone paging system via RS232. This requires connection to a Serial Interface provided by Multi-tone.
- Driver Setup:
Refer to the configuration document for step-by-step instructions on setting up the ESPA 4.4.4 driver.
Wiring Details
Multi-tone supports 3-wire, 5-wire, or 7-wire RS232 connections. For simplicity and reliability, a 3-wire connection is recommended.
- Recommended Wiring:
- Connection Type: 9-pin to 9-pin RS232
- Wires Used: TX, RX, GND
- Diagram: Refer to the screenshot below for visual guidance.
Additional Resources
- General Information on Remote Alarm Manager
- Remote Alarm Manager ESPA Driver Documentation
- Manuals and Setup Files