Communications failure due to transaction timeout when reloading b3 device
  • Communications failure due to transaction timeout when reloading b3 device
  • CraigEl
    CraigEl
  • David_Kendrick
    David_Kendrick
  • AbeMeran
    AbeMeran
‎2018-09-06 09:46 AM
Last Updated: Administrator CraigEl Administrator ‎2022-09-12 06:52 PM
Communications failure due to transaction timeout when reloading b3 device. b3's version number as seen from the Infinity side reads 0.0000
Andover Continuum
  • CyberStation
  • bCX4040
  • b3
A b3 BACnet controller is found to exist in the BACnet folder under an MSTP Network which is different from the Network specified in the bCX's comm2 Port.
Delete the MSTP network under the BACnet folder and perform a 'Find new BACnet devices'.  A new MSTP network should be created with the right network ID.