Checklist for maintaining or servicing a typical Continuum installation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Checklist for maintaining or servicing a typical Continuum installation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2791 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Checklist for maintaining or servicing a typical Continuum installation

Picard Product_Support
‎2018-09-11 01:20 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:36 AM

Issue

Checklist to be used as a basis for Maintenance visits.

Product Line

Andover Continuum

Environment

  • Continuum Hardware
  • Continuum Software

Cause

Having a checklist available for routine maintenance will help with service calls to ensure Continuum sites continue to run smoothly over the life of the installation.

Resolution

There is no official maintenance checklist but some of the things you might want to consider checking on a regular basis are the items below.

  1. Continuum Analyzer
    Run the tests which check the database for known issues and provides a results file. See How to run Continuum Analyzer and get a report.
     
  2. Review Windows Event Logs
    Check the Application and System Event logs for Continuum or SQL related errors. See Viewing, Saving, Sharing Windows Event Logs for Troubleshooting Purposes.
     
  3. Check the size of the ContinuumDB
    The Database can't be more than 2GB in MSDE, 4GB in SQL Express, and the size of available space on the drive if using full SQL Server. Continuum will always run better when the database is kept trim, as the database size grows, Continuum transactions may start to slow down. If general system slowness is observed then check the database size and SQL Server resources first.
     
  4. Truncate/trim event tables in ContinuumDB
    Especially the ExtendedLog table which can grow very rapidly if not kept in check. See Set up a Continuum system to do automatic log truncation to save database space.
     
  5. Check that the Continuum Workstation is patched and up to date
    Periodically service packs and hotfixes are released for different versions of Continuum to resolve identified issues. Consult The Exchange Download Center for the current updates.
    Service Packs | Hotfixes
     
  6. Check that Controller Firmware is up to date
    Check that the Controller firmware versions are supported for your version of Continuum and that they are up to date. Same as service packs for Continuum, new firmware builds are released as issues are identified and resolved. You can find supported firmware for each version of Continuum in the Compatibility Matrix. See Software and Firmware compatibility matrix for older versions of I/NET, Vista, Andover Continuum, Sa....
    And new firmware updates are available on Exchange Extranet.
     
  7. Check battery charges
    On controllers that have them, check that the battery for holding up the active RAM still has a charge.
    How to check -> Battery life in Andover Continuum controllers that have onboard batteries
    Replacement batteries -> Replacement batteries for the various Continuum controllers
     
  8. Run the Continuum Errors listviews to see if there are any recurring errors that may need to be investigated.
     
  9. Most Importantly - Backup the ContinuumDB before leaving site!
    Backup and restore instructions for a single-user system are below but these also apply to full SQL Server using Management Studio. Steps 1 and 2 in the article below apply to backing up a ContinuumDB. See Move / Backup / Restore a database on a Single User SQL2005 Express system.
Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 12457
  • troubleshoot
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore