How to run Continuum Analyzer and get a report
  • How to run Continuum Analyzer and get a report
  • Dave_Shore
    Dave_Shore
  • CraigEl
    CraigEl
‎2018-09-10 03:17 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-08 07:54 PM
How do I run Continuum Analyzer and get a report
Andover Continuum
Continuum 1.7 onwards
The Continuum Analyzer is designed to provide installers and troubleshooters with a point of reference for discovering problem areas within their installations.  The software is proactive in that it enables you to 'clean' orphaned and mismatched objects from the database, thereby recovering from a minimal amount of database corruption.  Continuum Analyzer also performs a system information check and provides full reporting on all aspects of the installation, as well as alerts regarding deficiencies.
Always ensure the site database backed up before Continuum Analyzer is used to "Clean" the database.
  1. Go to - Start - All Programs - Continuum - Continuum Analyzer
  2. Type in User Name and Password (usually andover97 and (not disclosed due to public access)) for the Continuum DB or you can use the system admin user name and password.
  3. Click on the version "System Tests", then "Run Wizards"
  4. There should be zero failed. Then "Generate Report". To save click on top left disk icon and save as .html file
  5. If there are any failures, then ensure the database has been saved before a "Clean" is performed
  6. There was a bug in some Analyzer versions that caused a ghost alarm on the AlarmInfo test, also see Continuum Analyzer Failure for Continuum 1.92 & 1.93
  • 6226