Set up a Continuum system to do automatic log truncation to save database space

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Set up a Continuum system to do automatic log truncation to save database space
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2899 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Set up a Continuum system to do automatic log truncation to save database space

Picard Product_Support
‎2018-09-07 01:44 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:58 AM

Issue

How do I set up a Continuum system to do automatic log truncation to save database space?

Product Line

Andover Continuum

Environment

Continuum Trend logs

Cause

Database maintenance.

Resolution

Setting up Automatic Log Truncation with SQL Server and MSDE Database 

MSDE Engine

For MSDE, you can download the Stand Alone MSDE Database Utilities from Buildings Download Center. 

These utilities are capable of automatically truncating the logs, as well making automated backups, checking for low hard drive space, etc. 

SQL Server

For full SQL Server, you can easily create a scheduled Job. Details are described below.  

To create a scheduled Job that will truncate the Continuum logs in the SQL Server:

  1. Open up SQL Enterprise Manager  (Note that the SQL Server Agent service must be running in order to create a Job)
  2. Highlight the Continuum database
  3. From the Menu, select Tools \ Job Scheduling
  4. A wizard opens: "Welcome to the Create Job Wizard." Click Next
  5. Select Transact-SQL Command,  Click Next
  6. For the Database Name, select ContinuumDB (or whatever the name of the DB is)
  7. In the large white space for the Transact-SQL Command, cut and paste the code from our web site:
    ****** Replace 90 with the number of days to maintain in each log ********
    delete from accessevent where DATEDIFF(day, timestamp, getdate()) > 90
    delete from activityevent where DATEDIFF(day, timestamp, getdate()) > 90
    delete from alarmevent where DATEDIFF(day, timestamp, getdate()) > 90
    delete from errorevent where DATEDIFF(day, timestamp, getdate()) > 90
  8. Click Next
  9. On the next screen, you are asked when you do want to run this job
  10. Select "On a recurring basis" and hit the Schedule button
  11. On the Schedule page, set up whatever schedule you desire
  12. Click OK to close the Schedule Page • Click Next
  13. On the Job Notifications screen, you can choose (if you want) any email or net send alerts. This is optional • Click Next
  14. In the final page, you are given a summary of the Job you have just created and you can change the name of your Job to anything you want. It might be a good idea to give it a more descriptive name like "Weekly Log Truncation"
  15. Click Finish and you are done. You should get a message that the job was created successfully.
  16. To verify that the Job is running correctly, you can go to the Enterprise Manager of SQL Server and click on the Management Folder, then expand the SQL Server Agent folder and click on Jobs. On the right-hand pane, you will see a list of created jobs. Scroll down and find the job that you just created. You can get information about the history of the Job, whether it ran successfully or not.
Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 2107
  • ChrisAsbury22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore