Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Changing the BACnet MAC address of the Multical meters

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Changing the BACnet MAC address of the Multical meters
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • RyanSuar
    RyanSuar
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3165 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Changing the BACnet MAC address of the Multical meters

Picard Product_Support
‎2018-09-11 07:09 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 12:51 AM

Issue

Changing the BACnet MAC address of the Multical meters

Product Line

Field Devices

Environment

Multical 601/602 with BACnet MS/TP module

Cause

The default BACnet MAC address of the BACnet MS/TP module has to be changed for BACnet integration to a BMS system

Resolution

Requires the USB Optical Eye tool (part number: MAOPTICUSB) and the software tools of the METERTOOL HCW or the Module Programmer. Both the METERTOOL HCW and the Module Programmer can be used to change the BACnet MAC address. The METERTOOL HCW is a program that installs SQL Server whilst the Module Programmer is a simple and lite program with limited functionality. So for the purpose of changing the BACnet MAC address, the procedure to change the BACnet MAC address using the Module Programmer is shown in this article. 

Install the USB drivers for the USB Optical Eye tool before connecting the tool to the laptop for the first time. The Module Programmer software must be installed after the Optical Eye hardware has been recognised by the computer.

  1. Remove the protective magnet from the Optical Eye and place on the front of the meter that we want to change. The Optical Eye sits over the bottom left corner where the small window is, resting on the 2 nipples, magnetically held.
  2. Launch the Module Programmer software. If not already shown, select the Com port which says Kamstrup USB Controller.1.JPG
  3. Press the Read button, this should return the Meter Type and Module Placement. If you are using the MULTICAL 602 and have fitted the module into the base of the meter2.JPG
  4. Select the correct Module Type from the drop down list. Here you must select BACnet because this is what you have.
  5. Press the same Read button again, it will read out the current setting. This is the MAC address of the meter for the BACnet MS/TP network.3.JPG
  6. If you are using the Schneider Electric AS/AS-P, the number must be less than 127. Use the UP/DOWN arrows to change address value or enter the number in this field manually. Press the Write button to send the new MAC address to the meter. It is best to power cycle the meter after changing any settings with this programmer tool. You can press Reset and prepare for new meter button and repeat the above steps.
  7. Read the address to verify that the new setting has been successfully written to the meter.
* Contact Product Support for the software and drivers.
Labels (1)
Labels:
  • Field Devices
Tags (2)
  • Find more articles tagged with:
  • 18299
  • mstp
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore