Changing from the "Small Numbers" format to the "Large Number" Format

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Changing from the "Small Numbers" format to the "Large Number" Format
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • DavidFisher
    DavidFisher
  • AdamSteele
    AdamSteele
  • Tom_Poovey
    Tom_Poovey
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4071 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Changing from the "Small Numbers" format to the "Large Number" Format

Picard Product_Support
‎2021-01-14 07:53 PM

Last Updated: Guinan AdamSteele Guinan ‎2025-01-07 07:24 PM

Issue

Need to change from the Small Number Format (Card Number) to the Large Number Format (Facility Code + Card Number).

Requirement for Security Expert Transitions with I/NET Hardware.  

Badging card on SCU1284 Reader using Security Expert, the reader event displays "Format error RD xx Port x Error Number of Bits"

From Security Expert Client EventsFrom Security Expert Client Events

Product Line

TAC INET, EcoStruxure Security Expert

Environment

  • I/NET Seven
  • Security Expert Transitions

Cause

The I/NET system is limited to a maximum number of access cards, 32,000 per Tenant.  If a larger number is required, then I/NET must be configured to use large card numbers. 

The Large card number format described in the Resolution MUST be completed before transitioning from I/NET to Security Expert and utilizing the I/NET SCU hardware as detailed in the Transition Guide Security Expert - INet Access Control to Security Expert - Reference Guide.

Resolution

To convert I/NET to use the Large Card Number support, the following steps must be performed: 

Conversion of Card Numbers (small) to Large Numbers

  1. Sort the Individuals list according to the Individual Number. Look in the Individuals Editor “Options” function to set this up.
    Step 1.pngStep 1a.png
  2. Look at the tenant editor to determine the Tenant Code/ Facility code of the cards.
    Step 2.png
    From this, use the circled items the Tenant Code (Facility Code) and the First Individual Number as the lowest possible card number in the next step. 
  3. Verify in the door editor that the cards in this system are in a known Wiegand bit format.  In this case, we are using 26-bit.
    Attached are various Excel spreadsheets that can determine the Decimal number of the first card in the system (e.g., Card #970 Facility code 199) is the Decimal number 13042634, using a 26-bit Wiegand Excel spreadsheet.  This number will become the Source number in the Key/Card Translation table.
    These include
    1. 26-bit
    2. 32-bit
    3. ABA115 format
      Step 3.png
  4. Create a Key/Card Translation table similar to that shown below in the I/NET Seven Access Control editor.  This table will be removed after running the provided SQL Script. 
    The Key/Card Translation must contain:
    1. Source - Decimal number calculated in Step 3 above (13042634)
    2. Target - First Individual number shown in the Tenant (970)
    3. Count - Number of Individuals as shown in the Tenant (10000)
    4. Tenant - Tenant number this translation refers to (1)
      If there are multiple Tenants, then this process MUST be repeated for each Tenant
      Tenant Editor and Key/Card Translation EditorTenant Editor and Key/Card Translation Editor
  5. Shut down I/NET completely and run the attached SQL Script. Then once the script runs then, restart I/NET and look in the Individual Parameters editor, as shown below.
    1. Start I/NET and delete the Key/Card Translation table create above.
    2. Open the Individual Parameters and verify a Hex number and the decimal number matching that from the Excel spreadsheet (Step 3) is seen in the Individual Editor Card section.
      NOTE: There may be multiple card entries here; the Last entry shown is that entered by the SQL Script.  It will depend on whether an existing Card entry was entered for the Individuals before running the SQL Script. 
      Step 5.png
  6. To have large numbers working on a site
    1. DipSw #7 has to be turned ON for the 7910/7920 DPUs.
    2. For the SCU1284 in the door editor, at the top center of that editor, there is a check box, "Card Translation," which has to be enabled for large numbers to work in the SCUs.
      Step 6.png
    3. An SLI “SAV” should then be done because that is where the Card numbers and Door settings are stored.
    4. Then perform an SLI restore.
    5. Followed by a DPU restore to all of the door controllers.
      NOTE: Steps 6d. and 6e. are NOT required when performing the transition to Security Expert as this information will be performed by the SP-C. 

 

Labels (2)
Labels:
  • EcoStruxure Security Expert
  • TAC INET
Attachments
BigCardConvert.zip
Tags (4)
  • Find more articles tagged with:
  • 7338
  • AdamSteele25
  • RobertAndriolo21
  • RobertAndriolo23
Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore