Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Cannot see a remote I/A Series BACnet/IP network while connected over a VPN connection.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Cannot see a remote I/A Series BACnet/IP network while connected over a VPN connection.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • Product_Support
    Product_Support
  • sesa116873_brid
    sesa116873_brid

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3723 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cannot see a remote I/A Series BACnet/IP network while connected over a VPN connection.

Picard Product_Support
‎2018-09-06 01:14 PM

Last Updated: Sisko GavinHe Sisko ‎2023-05-03 06:11 AM

Issue

Connected to a remote site network via WorkPlace Tech and a VPN connection, but unable to see the sites BACnet devices. No I/A Series MNB-1000s, or any 3rd Party BACnet devices, are found in Workplace Tech or the Commissioning Tool.

Product Line

TAC I/A Series

Environment

  • MNB-1000
  • WorkPlace Tech (all versions)

Cause

The VPN does place the connecting WorkPlace Tech PC on the site network, but the BACnet/IP (MNB-1000 and 3rd Party) devices are on a different subnet then the subnet assigned to the WorkPlace Tech PC.

Resolution

When BACnet/IP devices are on different subnets, BBMD must be used in order for the BACnet/IP devices to communicate across IP subnets. Only one BACnet/IP device can be enabled as BBMD per subnet.

 

Setup the MNB-1000 as a BBMD device using the Commissioning Tool

  1. Open Device Properties of the MNB-1000 controller and select the IP tab.
  2. For Device Type select BBMD and save change.

Setup WorkPlace Tech to connect to the BBMD device

  1. Select Tool from the WPT
  2. Select Configure Communication…
  3. Select BACnet and click on Change
  4. Select IP and click next
  5. Select Access a remote internetwork.
  6. For Host BBMD Address, enter the IP address of the MNB-1000 which was setup as a BBMD device. Click the Finish button to save changes.

You should now be able to see and connect to the I/A Series and 3rd Party BACnet devices using WorkPlace Tech.

Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 6272
  • DavidKendrick23
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore